What size copper conductor is required for a branch circuit using type THHW 75C conductor installed in a raceway that contains not more than three current carrying conductors and drawing not more than 30 amps?

Prepare for the Kansas Mechanical Journeyman Test with our comprehensive study tools. Use flashcards and multiple-choice questions, each including hints and explanations, to help you pass confidently!

To determine the correct size of copper conductor for a branch circuit using type THHW (Thermoplastic High Heat Resistant Water-Resistant) insulation with a temperature rating of 75°C, it is essential to refer to the National Electrical Code (NEC) and the ampacity tables specifically for copper conductors.

For a branch circuit that carries a maximum of 30 amps and has no more than three current-carrying conductors, the NEC allows for a specific size of conductor to be used safely without exceeding its rated capacity. According to the NEC ampacity tables, a 10 AWG copper conductor is rated for 30 amps at 75°C. This means that a 10 AWG conductor can safely carry the load without overheating or being at risk of failure.

In contrast, a 12 AWG conductor would be insufficient for a 30-amp load, as its maximum rating at 75°C is only 20 amps. Using it for a 30-amp circuit would not comply with safety standards and could lead to overheating or fire hazards. The larger sizes, such as 8 AWG and 6 AWG, while they can carry more current, are not needed in this scenario where the load is 30 amps